identify service fuse | on ElectriciansForums
Discuss identify service fuse in the UK Electrical Forum area at ElectriciansForums.net
oxfordshire
can anyone help me identify this service fuse please.
should I replace it with something more suitable ?
[ElectriciansForums.net] identify service fuse
Unless such a thing as a rewireable BS1361 fuse exists, in which case it would not be a BS1361 fuse I would guess that is a ruptured fuse which has been "repaired", a long time ago by the look of it.
hi it came from 1920's or 30's house with the seals intact also the fuse carrier has the same washers , so I'm thinking it's not been modified , I'm thinking to replace it with a 40a something ? I've installed a10kw shower onto it so so have to see what happens
The seals clearly aren't intact from the fact that have a picture of the fuse removed from its holder.
What you do is put it back and contact the DNO if you have any concerns about the condition of their equipment.
Don't take it upon yourself to interfere with, repair, replace or 'upgrade' DNO equipment!
Put it back exactly as it was, do not change anything, contact the DNO if you have any concerns about their equipment.
Like I say, a photo, then someone will have an idea. Everyone's guessing...
The DNO would almost certainly replace the cutout if thats the main fuse.
Would also add that replacing the existing with a newer fuse at a higher rating can go horribly wrong.Not all cut outs are rated for 80 or 100 amps etc...
Have seen images of melted cut outs where somebody put a 100amp in a 60amp rated cut out. numpty had changed the fuse, installed 2 car chargers, and had a couple of power showers...
its fitted back in the carrier and head, i was looking for a part number to put on the cert. it was such a loose fit and I was worried it may get hot with the new shower, so I bent the carrier prongs to make it tight. max fault current was 750A which went upto 850. will get customer to contact dno. help appreciated
Why would you risk a potential arc-flash incident which could leave you blind or worse, and risk exposure to asbestos containing materials which could kill you very slowly and very painfully just to get a number to put on a piece of paper?
Why not just record it as not verified, carry out your calculations based on the worst case 100A fuse?
Removing service fuses, especially very old ones, can be dangerous and is just not worth the risk for the sake of writing a number on a bit of paper.
Reply to identify service fuse in the UK Electrical Forum area at ElectriciansForums.net
R
Can anyone help me identify these bathroom taps please? Hi Can anyone identify the make and model of these taps please? We have one dripping...
Richt5a
R
W
Definitely agree that you should leave well alone and contact UK Power Networks to sort it out. It is their problem and why should you pay an...