Something between 0.75 and 25mm…..🙂

Profile says you have 2391, so this should be straightforward…if you’ve got your 18th to hand. But maybe you don’t have much experience with 3ph stuff??

Have a think…

What size of cable would you need for single phase 45A?

Does 3ph rating mean 3 TIMES 45, or does it mean 45 ACROSS 3 phases? (Ie, 15 each)

Figure that out, then go into the 18th Ed tables for volt drop, and install method.
 
IS the OP certain that its 45amp per phase , as that is one huge fryer

Most catering fryers that I have wired up were roughly 13amps per phase and were wired in 2.5
 
With the skyrocketing price of leccy I am surprised schools aren't taking out all the high consumption appliances and just serve sandwiches and fruit
 
I think we're all fairly sure that this will turn out to be a 10kw / 13.5A/ph size of device, the only thing I find worrying is that this should be challenging to someone with 2391 under their belt.
 

Reply to I'll soon be installing a 45A 3 phase deep fat fryer at the school where I work. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
711
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top