P
padawan
HI all
I have read these forums for while now, i have always enjoyed reading them, and found them very informative. Finally i get my chance to post a relevant thread. To start i should probably introduce myself a bit, i am currently training to be an electrician, and I'm working towards my NVQ.
So my boss is letting me design an installation and if all goes well it will help to complete a chunk of my NVQ. I have put a rough plan together so far, and was hoping to run it passed you guys, to see if i am going wrong anywhere, or see if there are any hints or tips i can pick up.
The job is running a new sub-main out to an outbuilding (garage in this case), and installing a distribution board, lighting circuit and ring/radial socket circuit. The supply to the property is a TNS system, 80 A supply, with a double pole isolator fitted.
My plan is run 3 core 6mm SWA for the garage supply, from the house consumer unit on a 40a MCB. In the garage install 40a DP RCD, 6a MCB for Lighting circuit, and either 32a/,20a/16a for socket circuit depending on ring or radial. I will run the socket circuit in PVC trunking, and the lighting circuit in PVC conduit. As the SWA will have to be run underground to the garage approximately 5 meters i will use corrugated plastic ducting. On the house side of the SWA i might have to use an adaptable box fixed the external wall, and run 6mm T&E to the consumer unit, as will there be a few 90 degree bends needed which could be problematic with the SWA.
I have a ew questions.
1. As the system is TNS supply, it is fine to export earth to garage supply?
2. On the house side of the SWA am i right that i should i use an MCB so that there is no RCD protection, reducing nuisance tripping? Or should i use a RCBO to make sure the SWA in also protected?
3. Is is best to use 3 core SWA and use 3rd core for earth?
4. I know SWA needs to be glanded both ends, but do both ends need to be bonded to earth? or just the house side?
5. Extraneous conductive parts. Are steel roof trusses an extraneous conductive part? The garage is concrete walls, on a concrete slab. So the trusses are structural steel, but not in contact with the ground, I'm not exactly sure where they stand as an extraneous conductive part.
6. If the trusses are extraneous conductive parts, then am i right that i should bond them in 10mm to the small garage consumer unit, or does it have to be run back to the main consumer unit in the house?
7. Is it best to run a ring or radial socket circuit in the garage? I would prefer 16a radial, but was thinking i might have to go 20a or 32a ring main, as the property owner will want to run a couple of freezers and washing machine etc, which could be an issue with max demand?
8. Does my plan sound ok, or would you suggest a different route? maybe henley block or something?
If you guys think i am on the right track then i will get back to you tomorrow about cable calcs etc. At the moment I'm thinking 6mm SWA, 10mm bonding, 2.5mm2 T&E for power circuit, and 1.5mm2 for lights (possibly singles as run in conduit)
Thanks for reading, sorry my first post was so long lol
So my boss is letting me design an installation and if all goes well it will help to complete a chunk of my NVQ. I have put a rough plan together so far, and was hoping to run it passed you guys, to see if i am going wrong anywhere, or see if there are any hints or tips i can pick up.
The job is running a new sub-main out to an outbuilding (garage in this case), and installing a distribution board, lighting circuit and ring/radial socket circuit. The supply to the property is a TNS system, 80 A supply, with a double pole isolator fitted.
My plan is run 3 core 6mm SWA for the garage supply, from the house consumer unit on a 40a MCB. In the garage install 40a DP RCD, 6a MCB for Lighting circuit, and either 32a/,20a/16a for socket circuit depending on ring or radial. I will run the socket circuit in PVC trunking, and the lighting circuit in PVC conduit. As the SWA will have to be run underground to the garage approximately 5 meters i will use corrugated plastic ducting. On the house side of the SWA i might have to use an adaptable box fixed the external wall, and run 6mm T&E to the consumer unit, as will there be a few 90 degree bends needed which could be problematic with the SWA.
I have a ew questions.
1. As the system is TNS supply, it is fine to export earth to garage supply?
2. On the house side of the SWA am i right that i should i use an MCB so that there is no RCD protection, reducing nuisance tripping? Or should i use a RCBO to make sure the SWA in also protected?
3. Is is best to use 3 core SWA and use 3rd core for earth?
4. I know SWA needs to be glanded both ends, but do both ends need to be bonded to earth? or just the house side?
5. Extraneous conductive parts. Are steel roof trusses an extraneous conductive part? The garage is concrete walls, on a concrete slab. So the trusses are structural steel, but not in contact with the ground, I'm not exactly sure where they stand as an extraneous conductive part.
6. If the trusses are extraneous conductive parts, then am i right that i should bond them in 10mm to the small garage consumer unit, or does it have to be run back to the main consumer unit in the house?
7. Is it best to run a ring or radial socket circuit in the garage? I would prefer 16a radial, but was thinking i might have to go 20a or 32a ring main, as the property owner will want to run a couple of freezers and washing machine etc, which could be an issue with max demand?
8. Does my plan sound ok, or would you suggest a different route? maybe henley block or something?
If you guys think i am on the right track then i will get back to you tomorrow about cable calcs etc. At the moment I'm thinking 6mm SWA, 10mm bonding, 2.5mm2 T&E for power circuit, and 1.5mm2 for lights (possibly singles as run in conduit)
Thanks for reading, sorry my first post was so long lol