C

cstewart37

How's about this for a bit of shocking workmanship!!! I was called out to this today and to say I am furious is a understatement. This is a 6kw immersion heater on a Local authority site. Electrical works should only be carried out by qualified / accredited electrical contractors! How many faults can you see from the attached pictures?
1 - Wrong type of MCB fitted
2 - 20 amp DP isolator (Immersion load 26amp)
3 - 4kw load contactor for 6kw load
4 - Thermostats 16amp switching 26amps!!!
5 - No certification for works carried out
 

Attachments

  • [ElectriciansForums.net] Immersion Heater 6kw
    Faulty Electricals 25-03-2013 005.jpg
    74.9 KB · Views: 136
  • [ElectriciansForums.net] Immersion Heater 6kw
    Faulty Electricals 25-03-2013 004.jpg
    104.7 KB · Views: 116
  • [ElectriciansForums.net] Immersion Heater 6kw
    Faulty Electricals 25-03-2013 007.jpg
    65.4 KB · Views: 111
  • [ElectriciansForums.net] Immersion Heater 6kw
    Faulty Electricals 25-03-2013 001.jpg
    82.4 KB · Views: 107
  • [ElectriciansForums.net] Immersion Heater 6kw
    Faulty Electricals 25-03-2013 003.jpg
    145.6 KB · Views: 113
Our company was called out to investigate the complaint of no domestic hot water!

We being a SELECT contractor with qualified SJIB Electricians more than can be said for the muppets/contractor that have installed the wiring for the 4 new 6kw immersions!
 
Oh its terrible! Trouble is nobody cares, if the local authority are letting works like that go on in their own propertys then they obviously don't care about what goes on in properties that aren't there's part P is a joke, it needs to be scrapped!
 
Yes Part P has always been a TOTAL joke. What we need is to be the same as the GAS SAFE registered contractors- I.E. Electrical SAFE! Why is it fine to kill someone with incompetent persons installing hazardous electrical installs, yet the GAS industry has their trade well covered ?
 
mind you you see it all the time....crap work done by incompetant person`s....
quite a lot of 1s n 2s are recent DIY/incompetants work...not the original install....
i`v carried out ECRs on 15 ed installs and found them still good for continued service....but the `add onns`....lol...
 

Reply to Immersion Heater 6kw in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
954
I went with a partner. We're able to support each other and take time off knowing the other is at the helm. We split all profit 50/50 whether we...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top