How's about this for a bit of shocking workmanship!!! I was called out to this today and to say I am furious is a understatement. This is a 6kw immersion heater on a Local authority site. Electrical works should only be carried out by qualified / accredited electrical contractors! How many faults can you see from the attached pictures?
1 - Wrong type of MCB fitted
2 - 20 amp DP isolator (Immersion load 26amp)
3 - 4kw load contactor for 6kw load
4 - Thermostats 16amp switching 26amps!!!
5 - No certification for works carried out