Would you loop of an existing immersion heater spur for a new central heating spur or, would you run a seperate supply?
 
Install a single socket and put a plugtops on the immersion heater flex and boiler feed.
That way only one can be used, you don't normally need both on at once anyway.
Gas being cheaper than electricity the immersion is usually only used in an emergency.
 
1, I don't like immersion heaters on plug tops.
2, I wouldn't have both methods of water heating on the same circuit, as a fault in one could knock out the other.
3, The immersion heater is quite a large load, and it is recommended that such loads are placed on separate circuits.
 
Put them both on a 20 amp radial - immersion fused at 13 amps ( hope i`m not gonna start another row here about running 13 amps through a 13 amp fuse) and CH at 3 amps or 5 amps as required
 
Strangely enough it seemed to be a common practice to wire an immersion heater from a ring main circuit in the 1960s using a switched spur unit for isolation.

I have seen a quite a few overheated fuse holders over the years !
 
20 dp switch for immersion heater and dp sw fused spur @ 3a on a 2.5 radial would satisfy loading but why would you want to run 2 2.5 radials? Personally i would never run an immersion on a sw fused spur
 
Although many existing immersions have a swFCU. Often on a 15A 3036. I'd leave it as is unless there's a problem, but would install a 20A DP by choice.

99% of domestic ch systems will pull less than 1A - it's the pump that's the large consumer and these are rarely more than 150W. So, CH and immersion on a 16A mcb should present no problems. Both should have DP isolation (remember most FCUs are SP).
 
I have never seen an Immersion on anything other than a SFS. It is after all a 13 Amp fuse, surely theres a reason that all imm heaters draw almost exactly 13 amps

It was usual in the 60s to fit a small square 20A DP sw.
In the villages round our way where there is no gas people tend to use immersions rather than oil for hot water. I've come across many burned out swFCUs. Always replace with 20A DP sw.
 

Reply to Immersion heater and central heating on same circuit? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Article
This is an RSS feed of thread: Leaking cylinder around immersion heater Content of the thread: Hi. My hot water cylinder has a small leak. It's...
Replies
0
Views
227
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top