Octopus

All,

About 50% of the houses I've been in recently have had additional connections added to the immersion heater circuits. The most common is a socket or FCU for a shower pump.

In my mind BS 7671 says that water heaters should be on their own circuits.

Bearing in mind that the vast majority of people only use an immersion heaters as a back up, are there any occassions that such additions are permissable??
 
Murdoch appendix 15 advises that an immersion heater should not be fed via a ring main 1 (i), but falls short of saying that it should be on it's own radial, the appendix leaves that to (ii) where it names cookers, ovens and hobs with a rated power exceeding 2kw should be on a dedicated radial.

Now why in the IET infinite wisdom they decided to omit an immersion heater from equipment exceeding 2kw which is does in most cases from the dedicated radial design only they maybe able to tell us.

Personally if the immersion is on a 16amp protection device and is a 3kw unit I can see no problem if someone wanted to fit say a 700w power pump via a FCU.

Bottom line for me would be as long as the manufacturers did not ask for a dedicated circuit for the immersion, the pump would get put on with it and note up at the CU.
 

Reply to Immersion heater circuits with additional connections in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

  • Question
How did it go?
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top