Hi guys

I was called to a clients house today, because for a week they've had no hot water which is supplied by their immersion heater in the loft.

There is 230V L/N going into the timer, 230V L/N going from time to the immersion.

There is 230V L/N going into the thermostat, which is set to 60 degrees, and 230V L/N going to the elements. I turned the power supply off and disconnected the thermostat from the element. Tested the continuity between the elements with a reading of 19 ohms.

As far as I can see, the immersion should be working fine - I sat there for almost an hour with 230V going from the thermostat to the element - still no hot water.

I could hear a light clicking noise coming from inside the cylinder tank.

Has anyone come accross this before, I have no idea what the problem could be! Does anybody have any ideas.

Thank you so much guys!!!!

Kelly x
 
Had a very similar fault once. No obvious cause for immersion to not be working but when tested with a clamp meter it was taking no load. Only solution was to replace the immersion.
 
I would con checked the live and neutral through the thermostat from the fused spur to the immersion heater itself. I have had a few cases where the thermostat has failed with a high resistance.
 
Great!

Sparkystu - I don't have a clamp meter :( will keep that in mind as an option though, might pick one up tomorrow. where would i stick the clamp meter? around the cable running from the thermostat to the element?

sctp - sorry i'm bit of a beginner! are you saying to do a continuity check between live and neutral from the spur through the thermostat? what result would i be expecting to receive? Or rather, what would a high resistance be?
 
Probably get slated for this but a fool proof method of checking an immersion heater is to take off the neutral connection and put a connector on it, turn power on and put one end of test lamp on the empty neutral connection and one end on neutral connector. If you get a light (240 V) then you know the element is OK.

OK broad shoulders............
 
Great!

Sparkystu - I don't have a clamp meter :( will keep that in mind as an option though, might pick one up tomorrow. where would i stick the clamp meter? around the cable running from the thermostat to the element?

sctp - sorry i'm bit of a beginner! are you saying to do a continuity check between live and neutral from the spur through the thermostat? what result would i be expecting to receive? Or rather, what would a high resistance be?

The circuit must be dead for test. Yes resistance check from live and neutral through thermostat and immersion heater. Should be around 18-25 ohms for a 3 Kw immersion. If high then do resistance check across immersion heater direct looking for the same. This should show you what is at fault.
usually it's the heater element itself but change both heater and thermostat as a pair to avoid revisit.
 
does the element have a thermal cut-out in the element housing and not in the stat.?
 
Is your stat switching both Line and neutral ? It is normally the case that the stat switches only one side of the supply, on a single element heater, the stat would switch the Line supply only. In a dual element heater, the stat controls the neutral.
 
It could be that the element is open circuit but if you are hearing a clicking noise then sounds like the heater is working as this is the element heating up in the tank. Plus you cannot really check these without a clamp meter I had one for 25 years and it gave up so I bought a digital replacement for ÂŁ60 but for you guys starting off Scr3flux were selling them for ÂŁ8

Just checked they still have it for ÂŁ9 it also doubles up as a multimeter so enter 13489 into their search banner and then click to see if your local branch has one in stock and then you are looking for about 11-12 amps

Also you need to stick or hook the clamp on to either the live or the neutral cable at the heater not across the flex and not over L&N together
 
Last edited by a moderator:

Reply to Immersion Heater Mystery! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Article
This is an RSS feed of thread: Leaking cylinder around immersion heater Content of the thread: Hi. My hot water cylinder has a small leak. It's...
Replies
0
Views
229
S
  • Article
Immersion Heater Leak? Has anyone got any suggestions as to what is going on here? My 25 year old megaflo cylinder in the airing cupboard has a...
Replies
0
Views
204
SteveRobert5a
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top