Replaced one of these today and saw it had no thermal cutout on it. The new one was to BS EN 60335 and had the cut out.

Question is, these are rented houses, 5 in total and all have the old BS 3955 immersions, the landlord is planning to have EICRs done in the next month or 2, so will these older heaters result in code C2 on when the EICRs are done.

Just wondered if so then i'll give him the heads up and might get the job of swapping them all.:tt1:
 
Has been a code issue for a while and very easy to miss.....many old periodics didnt pick them up....I guess many new EICR's wont either. But you are correct,they should get a C2.
 
Yeah all the others must be working as he's had no complaints about them.

Thanks guys

Just browsing the new EICR on easy cert, and can't see where this would be coded. Thought it would come under permanently fixed current using equipment part?
 
Last edited:
Check the ESC guide on PIRs and EICRs. Was code 2, now C2.

This is a serious safety issue. About 3 years ago a small girl was killed in a council house when the immersion failed on, boiled the water in the DHW and sent it into the plastic tank above. The plastic tanks can't handle the hot water and it collapsed and came through the ceiling. The girl was extremely badly burned and died a few days later in hospital.
There was a right stink about it cos the houses were supposed to have been refurbed.

BBC NEWS | England | Somerset | Focus on baby death safety checks

Woman killed by boiling water pouring on to bed - Telegraph

BBC NEWS | England | Somerset | Echoes of previous scalding death
 

Reply to Immersion heaters to BS3955 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K
Whatever... I awoke this morning ready for an intersting and relaxed day at work at my local branch of the Men's Shed charity. " jobs pending...
    • Like
Replies
0
Views
190

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top