Hiya everybody,

busy night tonight on the forum !! Cowboy electricians not doing their job, Newbuild downlight queries !!

anyway, here is my one.

Got back from a callout earlier today, simple job, dimmer module blown, replaced, all ok.
On my way out, guy says to me " can you change the time for my immersion heater".

I had a quick look, its a small immersion cylinder, but the flex is on a 13amp plugtop and thats plugged into one of those socket timers "timeguard" I think was the name.

Is that ok, or do I need to advise him to put it into a proper fcu. I think you can get fcu with timers on them.

Regards,
Sav
 
An immersion heater must be connected to the supply by a double pole linked switch only.
The use of a plug top and socket outlet is not permitted. 554.3.3
 
Thanks guys,

I will call him tomorrow and advise him.
The wiring does look dated, although he has had an RCD board fitted recently, but was reluctant to show me the cert, saying that "your here for the dimmer mate "

Thats why I didn't pay too much attention to the immersion issue, but it was bugging me on the way home.

I will check out the Sangamo as per Andrews recommendation.

The best I can do is advise him and tell him to tell his "electrician", to sort it out, if he prefers !!!

Thanks again guys and have a great evening,
Sav
 
It was on the tip of my tongue Bugsy, but I thought "Sav , do the dimmer, get paid and get out"

He did say he was going to pay by cheque and I replied "vat will be added and I need your cheque guarantee card number as well" !!!

The cash came out almost immediately !!!!

Wanna be stroppy mate !!!
 
Unfortunately you cannot force a client to do anything.

As you were only changing the time on the clock, the only thing you can do is advise them on any paperwork you give them.
 
Hi Andrew,
Sorry for the late reply. Just got back from 5-a-side football !!

I explained the regs to him and also confirmed that it is a radial from a 16amp mcb (board is about circa 1995).

He assumes that I want to take money off him for something thats and quote " been working fine mate. another electrician put the timer for me about 5 yrear ago and no problem" !!

I tried to get the electricians name or see any certs etc, but was shown the door.

Why do people always think that we are going to rip them off !!

Also, the mention to customers of RCD protection on their new additional sockets or lights and its "thanks for the quote, but we dont need RCD protection, its been fine all these years" !!

Should we turn like the cowboys out there and just add extra sockets or lights or anything, without the need for protection, or to abide by the regs etc ?? I mean, the customer "will pay cash" !!

Tempting, I know and I must admit, I have thought about it, but have always walked away at the end. Fool or someone that cares and is proud of their work !!

Anyway, now thats off my chest,a quick question before I go, do you think the immersion will be ok on the 13amp plugtop??

Best regards,
Sav
 
Mine is on a plug top ...just noticed ...still I have only lived here for 6 years ....and have never used the electricity to heat me water


spose its tools out over the weekend ...again

meh im always being moaned at by the missis "you do plenty of work at work but when it comes to doing the odd job round the house you do bugger all"

shes only been waiting for an extra socket in the bedroom for 4 months well she can wait another 4 months she only wants it for an hair dryer
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Immersion on a plug top !!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Sav,
Last reply from
mogga,
Replies
15
Views
3,305

Advert

Back
Top