Either 3 things, voltage not going through stat, through thermal cut out switch, or its not pulling any amps and change the whole lot. But recently I have been having to reset LOADS of thermal cutouts. I know they trip because it gets too hot. My question is, why do they get hot enough to trip?
 
I have seen this problem very often. If they have another source of heat heating the cylinder, the water gets hotter then the stat is set to. I live in the country and use a back boiler to feed my cylinder in the winter, if the immersion switch is left on, the thermal stat will trip.
 
Have had this where a Im heater has had the stat changed with one that has a resetable trip on it, continus tripping, all IR tests ok... Found to be that the tank was so old that the bottom Heater was not sitting in water but a pile of old scale 5 inches deap...Plumbers miss this even if they just change the element, as they are not expecting to see so much scale.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

J.C.E

Arms
-
Joined
Location
Earth

Thread Information

Title
Immersion thermal cutout
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
J.C.E,
Last reply from
Edd,
Replies
4
Views
2,331

Advert

Back
Top