Thermal cut out kept going on immersor stat so changed the stat over, now the new one keeps having the same issue. Any ideas on what it could be?? Could be another faulty stat but I highly doubt that
 
First one of these I dealt with on my own the tenants had turned up the thermostats on both elements. The boost thermostat was high enough to trip the thermal cut out on the night time element but only if the tenants boosted two hours in a row.

I thought I was going mad.
 
Probably not applicable, but is there another method of heating the cylinder?
Many of my customers have Rayburns or woodburners also heating the cylinder, When these safety cut outs were first introduced, I was plagued by callouts to reset them, as the alternative source regularly heated the water to a temperature that would trip it out.
Not so many calls in recent years. I don't know if that's because the cut out temp. spec. has increased (doubt it), customers have learnt not to let the water get too hot, or they've just learnt to reset themselves (probably).
 

Reply to Immersor stat fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K
Combi boilers don't normally have zone valves. What is the model of boiler?
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top