Installed an Immersun with a 1kW immersion last week. Immersun would not initialise as 'heater not detected'. Second Immersun behaved the same. Swapped over to the upper 3kW immersion on tank and Immersun initialised fine. Swapped back to lower 1kW immersion and Immersun worked, but after 20 mins said 'water hot' even though it was not and it was still supplying power to the immersion. After an email exchange with Immersun it is a 'feature', and they have issued a new firmware version that will allow loads down to 250W and will update if I send it back to them.
It is a bit of a pain as the customer is an hour away, but at least Immersun recognised the issue. A bit naughty as there is no 'minimum load' in the specification only a 'maximum load'.
I thought some might wish to be aware.
It is a bit of a pain as the customer is an hour away, but at least Immersun recognised the issue. A bit naughty as there is no 'minimum load' in the specification only a 'maximum load'.
I thought some might wish to be aware.