Hi all i am planning on using a consumer unit change in my own home for an assessment and am a little unsure on the following:

My cooker cable is 7/0.44 for the live and 7/0.36 for the cpc. Does anyone have the current carrying capacity for this cable?

Also is this the correct formula to find the metric csa equivelant?
The diameter of one strand in mm squared x pie / 4 and then multiplyed by the number of cores

Many thank`s
 
49A on an MCB or fuse, 37A on a 3036. (from 14th edition ratings tables).

It's 6.9mm csa conductors with 4.6mm cpc.

AFAIK this is not in the OSG
 
imperial was always better. don't know why we ever adopted the stupid metric system except to make it easy for morons who can only multiply and divide by 10.
 
Actually i have nothing against going metric, the only thing i don't particually like is the solid conductors of the smaller sizes of final circuit wiring. Makes pulling singles into conduit and the like a nightmare at times, they just ain't flexible enough, and are too prone to kinking etc...

But it does make me laugh at times, when the younger sparks amongst us think that the old imperial cable sizes are somehow inferior to metric sizes. When in reality most have larger current carrying capabilities than there so-called metric equivalents...lol!!!
 
and 7/029 didn't used to snap off at the terminations. either. another good reeason fot 4mm radials -- stranded.
 
and 7/029 didn't used to snap off at the terminations. either. another good reeason fot 4mm radials -- stranded.


Actually in the Far east, they use a stranded 3mm cable, for socket outlets and general small power circuits etc... wouldn't be a bad idea in my opinion, to adopt that size and type of cable/wires in UK and Europe.
 

Reply to Imperial cooker cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K
dreadful, I couldn't sleep at night after that install, it may just about pass but the quality of work is substandard IMO
Replies
4
Views
555

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top