Hello to all,
I've been asked by a customer to install an intermediate ( between 32a RCBO and first socket) switch so he can easily shut off all his workbench circuits at night. I've been looking for a 4 pole NC switch with a cover but I guess in the wrong place so far.
Any suggestions please?
Thanks
 
Welcome to the forum mate.
How about a contactor activated my a key switch?
 
I personally would not connect a ring final across a four pole switch/contactor due to the possibility of failure to one of the poles. I would change it so a 32A radial is taken to the switch then connect the ring final.

I was thinking of a 'forced guided' contactor.
Also a key switch so that only the person with the key can turn off the circuit.
 
I don't see how a force guided contactor would help, a four pole one normally has two n/c and two n/o poles.

If one of the contacts get stuck then they all will. As in your suggestion, you can still get a contact stuck and the other working, without one. It's a safer option.
 
But a four pole has opposing contacts, two n/o and two n/c doesn't it or am I getting this totally wrong.
 
But a four pole has opposing contacts, two n/o and two n/c doesn't it or am I getting this totally wrong.

The OP will have to look for a forced guided contactor that has 4 normally open contacts. Doesn't necessarily have to be '4 pole' could be '6 pole', as long as it has 4 normally open contacts.
Or he could go along your suggestion, then he only needs one that has 2 normally open contacts.
I just mentioned a 'forced guided' contactor mate.
 
What is the users intention?

Does he want to be able to clunk everything off under load as he leaves?

or..

Does he want to power everything down in a controlled and orderly manner before isolating the power to the circuit as a precaution?
 
Really need input from the OP as to what the customer requires on this. We have given him 3 options.
 
Hello, Spoon/Snowhead and all,thanks for all the input and welcome. I'd a bit more reading and a call to make..Yes, 'clunk off' is the deal. the guy is shutting up a big building each night, the benches have mebbe battery chargers, heaters and solders left on.
I looked at the rotary isolator which is the right kind of positive use design but not under load. Was thinking NC but that's relevant for emegency switch I think. This is a daily use device.
Thanks
 

Reply to In line switch for workbench ring in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
494
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

I thought I'd add a few photo's of the overall situation we find ourselves in and the general standard of the building work, which is why going...
Replies
9
Views
395
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
454

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top