I'm upgrading some main bonding prior to a board change, but got a quick question.

The incoming water supply is a metal pipe below the wooden floor in the living room, but the stop cock is in an inspection pit outside.

As I understand, the bonding has to be connected as soon as possible inside the property, but that means the bonding would be run to a clamp which would not be accessible without lifting the floor.

Current bonding is to a previous edition (15th I think) and is just connected to a random internal water pipe which is quite a way down the system.

What's the best way to proceed with this one?
 
The Regulations require extraneous-conductive-parts to be bonded.
It doesn't really matter where the connection is made, just as long as it's made.
With services, the requirement is to make the connection as close as reasonably practicable to where the service enters the premises.
This is a precaution against the connection being removed at some time in the future.
How likely is it that at some time in the future, the pipework with the bonding connection will be detached from the rest of the plumbing system?
 
In older houses in my area of the UK the water always comes into the house just as you come into the front door and that is where the stop tap is located, so there is always a hatch to allow you to get to the stop tap, thats where the bond should take place.
Now if its not accessable then as the other's have said fit it where it first comes out of the floor.
 
Last edited:
The Regulations require extraneous-conductive-parts to be bonded.
It doesn't really matter where the connection is made, just as long as it's made.
With services, the requirement is to make the connection as close as reasonably practicable to where the service enters the premises.
This is a precaution against the connection being removed at some time in the future.
How likely is it that at some time in the future, the pipework with the bonding connection will be detached from the rest of the plumbing system?

This is not correct......The reason the connection is required to be made at the point of entry,or first accessible position, is because the hazard the bonding is dealing with comes from outside the property,as long as the bond is made at the point of entry the hazard is dealt with and it does not matter what happens to the pipework beyond that point..But
if the connection is made further up the system there is a pssibility of an unbonded ECP between the bond and point of entry if an insulating insert or a poor continuity joint is installed.
If the service is bonded at the point of entry there is no possibility of the service being unbonded regardless of insulating joints/poor continuity joints unless the connection is physically removed.
 
Last edited by a moderator:

Reply to Inaccessible clamp on main bonding. Compliant? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
489

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top