hamit

hi everyone
3 phase mains coming into building split 1 phase for each of thee 3 flats. now 2 flats are converted into one and rewired my question is do i still use 2 phases for 2 fuse board to balance the load or do i use 1 phase and leave another one unused
any thoughts well appreciated
 
To be honest though not ideal I would rather have a spare phase on the system than having 400 volts in a domestic situation.

As it is now 2 flats, from 3 could you use that 3rd phase for communal areas, though it won't have the same load, it will still have some load on it.

Also it will enable you to use the one CU for the property rather than using the 2 just to use 2 phases.
 
Last edited:
You have the option of using only one phase (per flat leaving the third redundant) or you can have the DNO come out to change the service to a two phase supply. Mainly you need to make sure the neutral conductor size will suffice if you're to settle for the first option as I don't think it's going to be easy balancing 3 phase with 2 flats. Cheers
 
good advice sparks about the neutral size but I would imagine in a domestic situation it will be the same size as the LINE, but your right you need to make sure as it will be unbalanced, it can carry that load.

Once you start calling the DNO you can actually hear the pound signs rattle up over the phone lol, so I would try and utilise the 3rd phase for communal
 

Reply to incoming 3 phase in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
753

Similar threads

It won't be notifiable though as its not a new circuit, if you change the the tails from 16mm to 25mm is that notifiable? No, if you add an...
Replies
5
Views
431
What makes it a lack of space? I’d say to the customer to dismantle a cupboard or whatever to creat the space you need for the extra equipment...
Replies
1
Views
212

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top