Looking for some help with this one. Had a call to an apartment today, reporting a loss of power. Got to the job and sure enough nothing on the incoming tails. Went to the meter cupboard where we have a 3 phase incomer, going to banks of BS5419 100a isolators, then to the meter, then to a DP isolator, then the tails from there go through the fabric of the building to the flat about 30/40 meters away. We have 240v coming out of the isolator (L-N) but not at the DB. So, I isolated and removed L-N from the outgoing side of the DP iso and out of the main switch from the DB. IR tested the tails at the DB end, 0.01 at 500v and also a continuity reading between them (700ohms). Carried out the same test at the meter end, IR >999 and no continuity (as should be expected). So its appears that up to one point the cable is fine, and then it appears to have a dead short somewhere. So, if there was a dead short on the tails, Surely there would have been a rather large bang somewhere? Cant physically trace the tails as they disappear into the building in the meter cupboard and dont appear back till the DB in the flat. Building was constructed late 90's-ish. Any help here would be appreciated as the lad in the flat has 2 kids and no power!!