A
ambrad
Hi all, be gentle.
I have been asked to renew a cu so did some testing before commiting myself to the job.
The board is fairly old with breakers and main switch. I was doing a ins resistance test on a radial that fed 4 sockets in the kitchen and a two way board in the garage. The cable at the board is 6mm and goes under the floor and reapears at the sockets and garage in 2.5mm. There appears to be a jb under the kitchen floor that is covered in expensive lino, glued down.
When i did my test i got a slow reading >999 for the line/neutral and line /earth but a reading of 0.00 for earth/neutral. I believe this is a short caused by touching cables in the jb i cant get to or damage to the cable with a screw or nail bridging the earth/neutral.
Have i read my meter correct and therefore my damage assumption is correct or is there something else that could be the problem.
My issue is i cant get to the jb to check it. Should i suggest a rewire of this circuit to allow me to fit hte new cu with working rcd,s.
Thanks for any help
Thanks for any help