Hi all,
can anybody help me out?
ive been investigating an intermittent fault that causes the bottom rcd of a 20 way dual rcd cu to trip approx every 8/10 days. (Really annoying fault to trace)..
i used a mili amp clamp meter today to measure the leakage to earth from the bottom row and got a reading of near to 30ma (strange as the rcd trips on ramp test at about 25ish)
however when I started to isolate circuits to see if I could see if a circuit was excessively leaking to earth nothing much seemed to change on the metre reading... I then started to disconnect the cpcs one at a time to see if I could cause the reading to drop...
when I disconnected the cpc for the induction hob circuit (40 amp 10 mm feed) I saw an arc from the cpc to the earth terminal bar (I know you shouldn't disconnect cpc when live but scratching my head here!) I then went to put the cpc back in and as I touched the copper to straighten it I received one of the finest belts in my history as a spark!!! I then carried out IR test on my feed and everything was clear.. I then removed the isolator under the hob and tested here ...and as I clamped my leads on my cpc and then the earth from the hob my meter showed 192 v and 50 hz??? ( meter was in series so in theory I shouldn't of had a reading?) is there some serious capacitors inside the hob? And if so why when I splashed the cpc didn't the arc stop it was continuous? Hope this makes sense any ideas greatly appreciated!!
thanks in advance
jamie
can anybody help me out?
ive been investigating an intermittent fault that causes the bottom rcd of a 20 way dual rcd cu to trip approx every 8/10 days. (Really annoying fault to trace)..
i used a mili amp clamp meter today to measure the leakage to earth from the bottom row and got a reading of near to 30ma (strange as the rcd trips on ramp test at about 25ish)
however when I started to isolate circuits to see if I could see if a circuit was excessively leaking to earth nothing much seemed to change on the metre reading... I then started to disconnect the cpcs one at a time to see if I could cause the reading to drop...
when I disconnected the cpc for the induction hob circuit (40 amp 10 mm feed) I saw an arc from the cpc to the earth terminal bar (I know you shouldn't disconnect cpc when live but scratching my head here!) I then went to put the cpc back in and as I touched the copper to straighten it I received one of the finest belts in my history as a spark!!! I then carried out IR test on my feed and everything was clear.. I then removed the isolator under the hob and tested here ...and as I clamped my leads on my cpc and then the earth from the hob my meter showed 192 v and 50 hz??? ( meter was in series so in theory I shouldn't of had a reading?) is there some serious capacitors inside the hob? And if so why when I splashed the cpc didn't the arc stop it was continuous? Hope this makes sense any ideas greatly appreciated!!
thanks in advance
jamie