J

Jimathome

Hi all,

can anybody help me out?
ive been investigating an intermittent fault that causes the bottom rcd of a 20 way dual rcd cu to trip approx every 8/10 days. (Really annoying fault to trace)..
i used a mili amp clamp meter today to measure the leakage to earth from the bottom row and got a reading of near to 30ma (strange as the rcd trips on ramp test at about 25ish)
however when I started to isolate circuits to see if I could see if a circuit was excessively leaking to earth nothing much seemed to change on the metre reading... I then started to disconnect the cpcs one at a time to see if I could cause the reading to drop...
when I disconnected the cpc for the induction hob circuit (40 amp 10 mm feed) I saw an arc from the cpc to the earth terminal bar (I know you shouldn't disconnect cpc when live but scratching my head here!) I then went to put the cpc back in and as I touched the copper to straighten it I received one of the finest belts in my history as a spark!!! I then carried out IR test on my feed and everything was clear.. I then removed the isolator under the hob and tested here ...and as I clamped my leads on my cpc and then the earth from the hob my meter showed 192 v and 50 hz??? ( meter was in series so in theory I shouldn't of had a reading?) is there some serious capacitors inside the hob? And if so why when I splashed the cpc didn't the arc stop it was continuous? Hope this makes sense any ideas greatly appreciated!!
thanks in advance

jamie
 
Welcome to the forum.

Are you saying that if you clamp round the L & N feeding the bottom RCD and then turn off the MCB supplying the induction hob, that the differential current measured doesn't change significantly?
 
Sorry...I'm using a mili amp clamp metre around the earth of the install

If you're trying to look at why an RCD is tripping, you need to be measuring the differential current that the RCD itself is seeing. Clamping an earth conductor is likely to give all sorts of odd readings, depending on the earthing system, parallel paths, etc.

What is the earthing system?
 
EMI filters in induction hobs can cause high leakage due to capacitors from lives to CPC, this is normal. Whether it is too high will be determined by test as per Handysparks above. Capacitors do not influence IR test as that is DC.

E2A: Don't energise a circuit with its CPC disconnected. There is always a safer, alternative way to test it, whatever might be wrong with it.
 
Thanks for the advice....
asuming that the induction hob is (normal) and its some form of internal strange going ons how would you go about trying to locate the fault that intermittently takes out the rcd?
i was thinking of moving a circuit onto a rcbo above? To try and reduce the leakage on the bottom row of circuits?
 
might be an idea. put the hob on it's own RCBO, or, as a temp. measure, a non-RCD protected MCB. if the hob is the problem, then you'll have it verified after a while with no RCD trips.
 

Reply to Induction hob possible fault! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
520
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
460

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
661
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
962

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top