Morning all.
I'm in search of ideas.
Been installing an induction hob on a 6mm radial backed up by a 32a mcb. Came to power up yesterday and with all hobs on its throwing out the 30mA main switch rcd. (It's a TT system). Iv tested all my cables and there all clear so it's taking it out on earth leakage. I'm thinking there may be a few other items in the house with leakage and this is just taking it over the threshold. I have done a ramp test etc on the rcd and its fine.
The way I see it I can either put everything on rcbos and pop a main switch in or 100mA time delayed. Or split load DB with 2 30mA rcds and separate the circuits. But they are both expensive options. Any ideas guys??
Or I suppose leave the earth disconnected JOKE!!
I'm in search of ideas.
Been installing an induction hob on a 6mm radial backed up by a 32a mcb. Came to power up yesterday and with all hobs on its throwing out the 30mA main switch rcd. (It's a TT system). Iv tested all my cables and there all clear so it's taking it out on earth leakage. I'm thinking there may be a few other items in the house with leakage and this is just taking it over the threshold. I have done a ramp test etc on the rcd and its fine.