Induction hob tripping 30mA rcd | on ElectriciansForums

Discuss Induction hob tripping 30mA rcd in the UK Electrical Forum area at ElectriciansForums.net

N

Npt88

Morning all.
I'm in search of ideas.
Been installing an induction hob on a 6mm radial backed up by a 32a mcb. Came to power up yesterday and with all hobs on its throwing out the 30mA main switch rcd. (It's a TT system). Iv tested all my cables and there all clear so it's taking it out on earth leakage. I'm thinking there may be a few other items in the house with leakage and this is just taking it over the threshold. I have done a ramp test etc on the rcd and its fine.
The way I see it I can either put everything on rcbos and pop a main switch in or 100mA time delayed. Or split load DB with 2 30mA rcds and separate the circuits. But they are both expensive options. Any ideas guys??
Or I suppose leave the earth disconnected ;) JOKE!!
 
No it's not tripping straight away. Only when I have 2+ hobs on. Nah only got a standard clamp meter and don't do mA. I'm off back in a bit because they've had the hob exchanged as they thought it was faulty so il try just leaving it on. If it is leakage that's not due to a fault how can I get round it without sounding like I just want more money and doing the options I said above.
Thanks
 
Yeh there always under like. But I don't fancy changing the rcd for one that could possibly be tripping at 27 for the extra 6mA and encounter the same problem. Il go back try this new hob. Try it on its own. If needs be pop in an rcd in an enclosure as you said
 
Have you considered the radical approach of ringing or emailing the tech support department of the appliance manufacturer and asking them whether this is normal, and if so what they recommend as a solution?

Their response my provide useful ammunition for you explaining to the client why you're charging them for installation of a new 11kV sub-station.
 

Reply to Induction hob tripping 30mA rcd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
520
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
460

Similar threads

  • Question
In all likelehood, no different. The RCD on the left is looking for electricity that is going missing in action. If the total missing reached...
Replies
3
Views
1K
Ok I’ll try this when I’m down
Replies
4
Views
369

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top