We have been asked to do a EICR on a small scale industrial installation.Am I correct in thinking that the inspection and testing should only involve the fixed wiring,(that involving small power,lighting,and supplies to machinery)but not such things as emergency stop circuits etc,fed from control panels etc.
 
The control circuits are beyond the scope of BS7671, so usually they won't be tested. You could include them in a visual though if requested?

The feeds to motors are usually tested upto the isolator, with only IR to the motor itself. Long lead test to confirm CPC!
In most industrial complexes the earthing won't be a problem due to paralell paths!
make sure you have the limitations written down & agreed before work starts.
 
Yes note all limitations and only test what you have been asked.
No harm in looking at the other electrical items and gathering readings from isolators etc.
You could also check that the lights and rotating machinery do not cause an issue due to "strobe light effect"
Also can do a functional check on emergency stops and has been said visually check them too make sure NC contact blocks on the back etc but take it as far as has been agreed
 

Reply to Industrial installation testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
933

Similar threads

For a new circuit or alteration the dead tests should be done first to ensure it is safe to energise.
Replies
3
Views
323
NICEIC Certification Scheme NICEIC Competant person scheme
This sounds very similar to me. My level 3 NVQ is in engineering maintenance and I also have a HNC in Operations Engineering. I’ve been working...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top