Maximum demand for cable then? Seems a bit of a strange setup. What about Isolation, other than a MCCB. Need to know the whole installation design?Thanks for the reply. Socket will supply a temporary building and and length of run from the power source to the socket will be about 15m max. Thanks
Hopefully, your socket is in an External; weatherproof Cabinet.
I think this whole scheme is madness to allow a third party access to your equipment to connect a 3 Phase supply of that rating.
I would be asking for more details of Mr Client's cabin Installation as to whether it is wired correctly & safe to connect to your socket.
Who is going to be liable?
I would not be happy installing a 125A socket outside without adequate protection & local isolation. I would also ask for details of equipment & maximum demand of the cabin installation, a question often asked by your DNO before connecting a supply. I would then feel that I have designed & installed a adequate installation to satisfy both parties needs.Why?
Why? Myself and a few other members do this on a regular basis, and with much bigger sockets than 125A.
Again why? Assuming the OP is being employed to install a socket circuit then their responsibility is to install a socket.
Do you always ask for full details for what is going to be plugged in when someone asks you to install a socket?
As far as liability the OP is liable for the socket installation, the builders of the temporary building are liable for that installation and the person who plugs it in/authorises the plugging in is liable for it being energised.
I would not be happy installing a 125A socket outside without adequate protection & local isolation.
I would also ask for details of equipment & maximum demand of the cabin installation, a question often asked by your DNO before connecting a supply. I would then feel that I have designed & installed a adequate installation to satisfy both parties needs.
This is only my personal opinion & way of working & I am sure that the OP will come to there own conclusions to follow. So far all replies are based on assumptions with lack of design information.