I've been asked about providing inline surge protection for the UPS supplies in numerous network cabinets around our factory and I'm hoping someone more experienced in this might have some suggestions.
There are about 15 cabinets dotted around the factory containing various switches and routers for all of the networked drives/PLC's/IO's etc. Each contains a UPS and a non-surge protected PDU. IT keep complaining that power surges (real or imagined) are killing the UPS's. They've asked us (maintenance) to fit some sort of surge protection inline with the supply, but I'm not entirely sure that's possible.
The UPS's draw 16A when charging after being fully discharged, they're connected to the supply DB in SWA via a 16A interlocked commando socket. I've not checked every DB but it looks like they're on a single phase 20A MCB in the DB's.
As far as I'm aware the best solution would be to fit a separate 3-phase type 2+3 SPD in an enclosure alongside each DB supplying a cabinet, which has the benefit of protecting all of the equipment connected to it. Not every DB has a spare way to fit an MCB to protect the SPD, which I think is regarded as best practice if not actually in the MI for the SPD's?
Alternatively could a single-phase type 2+3 SPD be fitted in parallel with the outgoing supply for the UPS, or is there some device I can fit inside the cabinets that would protect the UPS as well as the equipment after it?
Even better would be a truly inline solution like a surge protected 16A commando socket, but my trawling of the interweb hasn't dug one up yet, if they even exist at all.
There are about 15 cabinets dotted around the factory containing various switches and routers for all of the networked drives/PLC's/IO's etc. Each contains a UPS and a non-surge protected PDU. IT keep complaining that power surges (real or imagined) are killing the UPS's. They've asked us (maintenance) to fit some sort of surge protection inline with the supply, but I'm not entirely sure that's possible.
The UPS's draw 16A when charging after being fully discharged, they're connected to the supply DB in SWA via a 16A interlocked commando socket. I've not checked every DB but it looks like they're on a single phase 20A MCB in the DB's.
As far as I'm aware the best solution would be to fit a separate 3-phase type 2+3 SPD in an enclosure alongside each DB supplying a cabinet, which has the benefit of protecting all of the equipment connected to it. Not every DB has a spare way to fit an MCB to protect the SPD, which I think is regarded as best practice if not actually in the MI for the SPD's?
Alternatively could a single-phase type 2+3 SPD be fitted in parallel with the outgoing supply for the UPS, or is there some device I can fit inside the cabinets that would protect the UPS as well as the equipment after it?
Even better would be a truly inline solution like a surge protected 16A commando socket, but my trawling of the interweb hasn't dug one up yet, if they even exist at all.
- TL;DR
- Is there a way to provide inline surge protection for a 16A commando socket?