Inspect and Test Question | on ElectriciansForums
Discuss Inspect and Test Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Edinburgh
Hi all,
Probs a simple one here but when testing a 3 phase board for ze as part of a periodic inspection plus part initial verification of a small db supplied by this board should I note the main 3 phase ze within the supply parameters section of cert and then the small db as zdb within the schedule of tests? Or just use the main ze for both?
Studying for 2391-52 course
Cheers
Most recent NIC test sheets have it so your earth loop test carried out at the origin of supply would be your Ze. Earth loop carried out at the main switch in any fuse boards would be your Zdb
Zs would be your earth loop tests at end of circuits
Ze is the external loop impedance, so by definition it does not incorporate any part of the installation and can only apply at the origin.
Worth noting if you were completing an EICR on both these boards there would be a separate test sheet for each board and each sheet would have the supply characteristics at the top for you to fill in. so if you view it like that it will become more obvious. hope that helps.
Reply to Inspect and Test Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Check out pages 92 and 93 of GN3 for help.
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Recommended Sponsor News
thanks for the clarification. ( also thanks to Dan. ).
More info on link below http://sbsc.uk.net/