B

bks

why RCD trips when you do two lead low current test and doesn't trip when you use three lead tester. I am using MFT megger 1730 and less than year old. I am bit confused with it. I did RCD trip current test as well in case RCD is faulty and found 19ma trip current. tripping the RCD, is that meant there is fault somewhere or what. I did test insulation resistance which i got overall >2megha ohms and individual circuit > 200 megha ohms. There is fixed appliances like oven, washing machine and dishwasher etc. Love to hear more about it please.
 
Last edited by a moderator:
on the hi loop test you are shoving 25A test current L-E. this will obviously trip the RCD. using the lo loop test, a 15mA current is used. so as not to trip the RCD. because of the low current used, the reading is not as accurate as with a hi current test.

edit: misread OP. seems you are tripping on a 2 wire lo test. not knowing the 1700 series, can;t comment further.
 
on the hi loop test you are shoving 25A test current L-E. this will obviously trip the RCD. using the lo loop test, a 15mA current is used. so as not to trip the RCD. because of the low current used, the reading is not as accurate as with a hi current test.

edit: misread OP. seems you are tripping on a 2 wire lo test. not knowing the 1700 series, can;t comment further.
i think they had problems with thenm Tel...

this was sorted out....but it may be that the instrument he is using needs sending back to Megger for them to update the firmware...which i think they were offering free...
 

Reply to Inspection and testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
724
  • Question
As you said in #9 get an electrician involved. The information you are giving is not clear as you do not understand what is being asked which...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top