Hi just a bit of advise requires just had the submain cables upgraded to 16mm cable the electricians have wired them all into a standard consumer unit with one 100 amp main switch and then rcbos to the flats x5 does this sound right he has struggled to get them into this consumer and I'm worried about the 100 amp switch being overloaded also there are no 10mm earths run with the 16mm t and e.
the council have said the work looks shoddy. The electricians are coming back to address I just want to be sure all right.