Just have a temporary assignment at a chicken hatchery for a few months rubbish money but home by 3-30pm not much about anyway.Came across an installation that was fairly old and cable sizing is not right.A 3phase supply comes from a 32amp type 4 merlin gerin mcb wired in what looks like 10mm2 to a isolator 10metres away.From the isolator it goes to a contactor then to a din rail with connecter blocks.From the connector block it serves 12 6amp mcb's " in 1.5mm each radially fed i.e one 1.5 for each mcb and has not fused down also feeds a few other mcb;s relays heliwell temp guages not any high loading but obviously.So basically the 1.5 is only a short length of about 8" or so.Normally this would have been fed from the 10mm2 by a correctly rated bus bar.I know its not right but just wondered as the 1.5mm2 was such a short distance would this be o.k Thinking of similar examples unfused radial 2.5 spurs on ring mains which are 32amp mcb's ,I know effectivley the main loading is on a ring but it does eventually spur off and reduce to a radial 2.5 sized cable???? YOUR THOUGHTS would be grately appreciated