Just have a temporary assignment at a chicken hatchery for a few months rubbish money but home by 3-30pm not much about anyway.Came across an installation that was fairly old and cable sizing is not right.A 3phase supply comes from a 32amp type 4 merlin gerin mcb wired in what looks like 10mm2 to a isolator 10metres away.From the isolator it goes to a contactor then to a din rail with connecter blocks.From the connector block it serves 12 6amp mcb's " in 1.5mm each radially fed i.e one 1.5 for each mcb and has not fused down also feeds a few other mcb;s relays heliwell temp guages not any high loading but obviously.So basically the 1.5 is only a short length of about 8" or so.Normally this would have been fed from the 10mm2 by a correctly rated bus bar.I know its not right but just wondered as the 1.5mm2 was such a short distance would this be o.k Thinking of similar examples unfused radial 2.5 spurs on ring mains which are 32amp mcb's ,I know effectivley the main loading is on a ring but it does eventually spur off and reduce to a radial 2.5 sized cable???? YOUR THOUGHTS would be grately appreciated
 
Knew it was around there somewhere - 434.2.1; basically you can reduce the csa of the cable if it doesn't exceed 3m in length.
 
Many thanks sintra you are right mate and quoted regs no. but i must be missing something as i still cant get my head around it effectively the 1.5mm2 albeit short length is protected by a 32amp fuse and generally 1.5mm2 takes around 15.5amps what am i missing????
 
You are missing the bit that the 1.5mm is supplying a 6A mcb so the cable can not overload as it is limited to the 6A of the mcb.
 
I was sold the idea as being like using a thin bit of flex on a lighting pendant.

yes that is a reduction in the current carrying capacity but i cannot see how how it is protected against overload as in the op's example, you could overload the flex in the event of a fault with the lamp or holder.
 

Reply to Install/re-furb chicken hatchery in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Here's another website with lots of info regarding the AM2 AM2 Test – Pass It First Time - http://passam2.co.uk/ Michael
    • Like
2
Replies
31
Views
10K
Just in case I just bought a Megger MIT 330 on a great deal on evilbay as a stand alone tester too for every eventuality ! It was Westwards fault...
Replies
27
Views
6K
It will not achieve any discrimation - a short circuit will be seen by both the 20a rcbo and the 32amp mcb and is just as likely to take out...
Replies
8
Views
3K
S
  • Question
Hi guys, Been having a think about this one, and have come up with the following question. I'm wiring up the garage to the house supply...
Replies
0
Views
1K
steviec_lj
S
S
cudaboy, youre mate has a classic ?, is that a consul classic 315, cause thats what ive got !! regards dave:)
Replies
21
Views
4K
heathelect
H

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks