I've recently qualified but not yet a member of a 'competent person' scheme. Apologies for the verbose content...
I was requested to visit a friend of the family regarding the safety of a shower.
On inspection, the mira sport shower cover was not fixed (i.e. screw missing) and it was incomplete (i.e. had a pannel or a bit missing from its left side). The hole would allow more than a few fingers to be inserted into the shower unit let alone water spashes etc.
It's important to add here that the customer informed me that the shower unit was left like this by the electrical contractor who had changed the CCU. i.e. may not be true.
The NICEIC installation certificate showed comments on existing intallation as: Shower switch wiring showing evidence of overheating. So I asked the customer to show me the shower switch which he did but said that the contractor had not opened the switch. Again, this is what the customer said! Obviously the circuit was isolated at the CCU so I opened the switch cover to find strands of the 6mm unconnected, melted insulation and undisturbed soot in the bottom of the switch enclosure. Worse of all is the cpc was not doubled over and effortlessly fell out of its connector. The test results showed an acceptable earth fault loop so I guess the cpc did have a connection in the switch.
I took photos but was unable to upload them.
The customer had already been advised not to use the shower with the hole in its side which was heeded.
The customer has already aquired a new 9.5 kW shower which will require 10mm2 cable so I removed the 6mm2 circuit from the CCU leaving it dead. I'm confident that it's safe now.
My questions are:
Should I, or the customer, do anything regarding the validity of the safety certificate etc?
Should the electrician have inspected inside the double poled switch? if he had, he would have seen what I did.
Thanks for any assistance.
I was requested to visit a friend of the family regarding the safety of a shower.
On inspection, the mira sport shower cover was not fixed (i.e. screw missing) and it was incomplete (i.e. had a pannel or a bit missing from its left side). The hole would allow more than a few fingers to be inserted into the shower unit let alone water spashes etc.
It's important to add here that the customer informed me that the shower unit was left like this by the electrical contractor who had changed the CCU. i.e. may not be true.
The NICEIC installation certificate showed comments on existing intallation as: Shower switch wiring showing evidence of overheating. So I asked the customer to show me the shower switch which he did but said that the contractor had not opened the switch. Again, this is what the customer said! Obviously the circuit was isolated at the CCU so I opened the switch cover to find strands of the 6mm unconnected, melted insulation and undisturbed soot in the bottom of the switch enclosure. Worse of all is the cpc was not doubled over and effortlessly fell out of its connector. The test results showed an acceptable earth fault loop so I guess the cpc did have a connection in the switch.
I took photos but was unable to upload them.
The customer had already been advised not to use the shower with the hole in its side which was heeded.
The customer has already aquired a new 9.5 kW shower which will require 10mm2 cable so I removed the 6mm2 circuit from the CCU leaving it dead. I'm confident that it's safe now.
My questions are:
Should I, or the customer, do anything regarding the validity of the safety certificate etc?
Should the electrician have inspected inside the double poled switch? if he had, he would have seen what I did.
Thanks for any assistance.