Hi everyone was wondering if any one could help me out I've just done a board change and went to do an installation resistance test on the whole board it failed L-N so I found the fault on down stairs lights so took that out and did it again L-N >299 N-E starts at 172 then reaches 247 & E-L starts at 157 gets to 225 yet when I do each circuit separate all the readings reach >299 surly the whole board should be the same. Thanks Simon
 
when you IR the whole board, you are getting a reading of all the circuits in parallel. therefore, you would expect the reading to be lower than the individual circuits. think of resistors in parallel.
 
Firstly it will save you a lot of headaches if you IR test before you change the CU and quote accordingly for remedial work along with the CU change.

Secondly you're worrying about IR test results that are more than a hundred times better than required by the regs.
Finally the insulation resistances of each individual circuit will always be better than the global reading because the individual circuits are effectively in parallel.
 
I am totally astonished to be honest, absolutely astonished?
If you're equally astonished at 2 circuits that are in parallel (A1 & A2) then your overall astonishment (At) could be defined as At = A/n where n is the number of circuits you were astonished at so At would equal A/2 in this case.
 
If you're equally astonished at 2 circuits that are in parallel (A1 & A2) then your overall astonishment (At) could be defined as At = A/n where n is the number of circuits you were astonished at so At would equal A/2 in this case.

Aye, ok clivvor shyte ...... haven't you got a spear to sharpen & a grass skirt to iron somewhere??
 

Reply to Installation resistance testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
554
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
992
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
924

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
421
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
617

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top