Darkwood
This set up will only give load discrimination and not short circuit, if you intend to supply a submains which has spare ways you have to account that other loads are added, if your doing a dedicated board and have discussed this option with client then you need to know what your largest mcb rating is and find a comparison chart to a BS88 fuse that will give full discrimination, where this means your fuse is higher than the DNO cutout then there is little you can do but to cover with the largest BS88 you can fit regarding the KVA of the supply and give partial discrimination.
You seem to be trying to design without taking into account for discrimination of fusing, this can be costly to the end user if a fault occurs on a final circuit as there is no gaurantee that the final circuit mcb would trip before the 40amp Bs88 you propose.
Also why are you giving 4pole isolation?.. you will be fine with 3pole, if you do 4pole which is not required then ensure any device has early make/late break N operation or you could blow any electronics and control gear in the machinery (dependant on the machine) and any 1ph equipment could suffer damage too just with the action on switching a 4 pole device that covers multiple circuits.
You only require 4pole Isolation at the origin if it is highly likely that the untrained end user or other person may be using it for isolation purposes, this is why domestic has to have both L/N isolated because untrained ppl use the switch to turn the power off.
You seem to be trying to design without taking into account for discrimination of fusing, this can be costly to the end user if a fault occurs on a final circuit as there is no gaurantee that the final circuit mcb would trip before the 40amp Bs88 you propose.
Also why are you giving 4pole isolation?.. you will be fine with 3pole, if you do 4pole which is not required then ensure any device has early make/late break N operation or you could blow any electronics and control gear in the machinery (dependant on the machine) and any 1ph equipment could suffer damage too just with the action on switching a 4 pole device that covers multiple circuits.
You only require 4pole Isolation at the origin if it is highly likely that the untrained end user or other person may be using it for isolation purposes, this is why domestic has to have both L/N isolated because untrained ppl use the switch to turn the power off.