im installing a 3.96kW System on a farm. The main board in the house is roughly 100 metres away from where the solar panels are going to be placed.
they will be outside in a field where decking is being put down. i have measured up a 10mm swa cable buried will be suitable as ther is only a 2.8% voltage drop due to length of cable.
can i take the cable to a small 30mA RCD protected Garage Unit (small C.U) 16A breaker as an isolator, then to the existing house C.U to a 16A breaker? and would this have to be on an RCD also?