my sister has asked if i will install a shower for her when i have sufficient knowledge and experience.
iv been going through some figures as a little practice whilst im not very busy.
This is the CU set up
TNCS supply
------------CCU------------
downstairs sockets - 32A - 32A with diversity
downstairs sockets 32A - 12.8A with diversity
downstairs lights 6A - 3.96 A with diversity
upstairs lights 6 A - 3.96A with diversity
Cooker 32A - 16.6A with diversity
Heating 16A - 13A with diversity
total demand 82.32A
the supply fuse is 80A
before i even consider installing a shower in the future would the supply fuse have to be upgraded by DNO?