Hi,

I am currently working on a project where the client has asked us to complete a discrimination study.

The primary area of concern involves an upstream miniature circuit breaker (25A type C) and a downstream 10A gG fuse.

The type C circuit breaker time current characteristics within BS 7671 (Appendix 3, Fig 3A5) have been reviewed and it appears that the curves only exist for breaking times greater than 0.1s. I have a few questions regarding this:

  1. Why do the curves not exist for time frames below 0.1s?
  2. Is it correct to infer from the lack of data below 0.1s, that all instantaneous faults will last at least 0.1s?
  3. The time current characteristics of the 25A type C MCB and 10A gG fuse do not overlap. Is this sufficient to conclude that discrimination/selectivity is achieved for all fault levels or do other things need to be taken into account? I am particularly concerned about instantaneous faults.
 
Hi welcome to the forum.

Looking at the mcb curve in the regs you are given a box in top right of the page, this will stipulate a specific trip time related often to various regulations, so if you have a circuit that has a 5second allowance then you can refer the rating of device to the current required in a fault condition to ensure it trips in time, having information extending past 0.1 seconds serves little purpose as this will be classed as instantaneous.
Discrimination between devices means when you have a fault condition past a downstream device then that fault will take out the downstream device before any upstream devices, where devices are of a different nature you are best looking up a discrimination chart between different devices.
In a fault on your scenario I suspect only partial discrimination will be achieved, it can be however an issue to achieve full discrimination if your supply size to the premises is a limiting factor, in your case this not an issue relative to the small rating of the 10amp fuses, you may need to upgrade you supply and increase the 25amp though to ensure full discrimination, I cannot say though without comparative charts.

As an example of full discrimination, mccb - mcb then to ensure full discrimation on a mcb dist' board you would need a 160amp rated mccb.
 

Reply to Instantaneous faults and discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

  • Question
If they are standard RCBOs the MCB aspect could be b,c, or d , but the RCD aspect is almost certainly 30mA instantaneous. If the MCB aspect...
    • Like
2
Replies
22
Views
2K
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top