Is it possible to test Lightning Conductor with an Earth Loop Impedance Tester ?

Discuss . . . . . . . . .. .


You will be measuring a whole load of other carp, such as the line conductor all the way back to the transformer, some transformer winding resistance, the transformer earth mesh/rod/whatever AND the lightning conductor. How do you know what resistances are attributable to each part.

You don't need to drive 4' long test electrodes into the car park to get valid readings from a pukka earth resistance tester...
 
This particular installation is a Church surrounded by a tarmacked car park.
Also, to prevent theft of he copper rod, the electrode is contained in a steel tube to a height of approximately 4M.

Tarmac does not prevent a proper test being carried out. Surface contact electrodes can be used for the test connections, small piles of damp chain are often mentioned as a possible option
 

Reply to Instrument for Testing a Lightning Conductor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
I used 9mm earth rods with a right angle bend on the top and earth wander leads suitably sleeved to denote the different positions, worked out a...
Replies
1
Views
642
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top