P

Patrick Griffin

Hi lads,

When IR testing at a board I know i should expect a very high resistance between lives and earth but in a tncs system would i get a lower IR reading testing between N-E? The scenario im describing is one in which the tails are all connected but the board is isolated.

Cheers..
 
when im doing the insulation tests i always isolate the board and disconnect the earth whilst doing the tests , this eliminates any connection for instance if the isolator is single pole , shouldn't be but possible in the case of switch fuses three pole isolators on three phase boards etc



Have a look at 612.3.1 The test should be conducted with the means of earthing connected, be it the supplier's earth, or a local electrode. Otherwise you could have a fault to true earth e.g. a bit of a steel framed building, and it wouldn't show up in the test.
 
Have a look at 612.3.1 The test should be conducted with the means of earthing connected, be it the supplier's earth, or a local electrode. Otherwise you could have a fault to true earth e.g. a bit of a steel framed building, and it wouldn't show up in the test.

I read that as, between live conductors and any cable that will be connected to the earthing arrangement, not between live conductors and the MET as you imply.
 
I understand well. Testing is done with the boss. Testing domestic, commercial boards i have not done i understand these for the most part bar a few areas one of which i asked in this thread.

The confusion with this thread is i forgot that in the uk you have double pole isolation i was assuming it was like here in ireland where you have single pole isolation. I just wanted confirmation that the neutral or earth has to removed to break the n-e link in the tncs system.
Parts of this type of testing i had forgotten so i decided to started reading up on it and asking questions on this forum, it has been great until now.
Goodluck tony and thanks.
 
Last edited by a moderator:
I read that as, between live conductors and any cable that will be connected to the earthing arrangement, not between live conductors and the MET as you imply.

It wasn't my intention to imply the test is between the live conductors and the MET.

The test should be conducted "between live conductors and earth". Note that it does not say cpc) "Earth" has a very specific meaning in the regs. To perform the test properly, and to obtain a valid result, there must be a connection to "earth" at the time of test.

A nail through the line conductor only, into damp plaster, won't show up if the test is carried out with no cpc connection to earth, but it will show as low IR if the test is carried out between line and "earth" i.e. cpc connected to MET, assuming a valid means of earthing.
 
when im doing the insulation tests i always isolate the board and disconnect the earth whilst doing the tests , this eliminates any connection for instance if the isolator is single pole , shouldn't be but possible in the case of switch fuses three pole isolators on three phase boards etc

The cpc should not be disconnected. The means of earthing should be intact before conducting the test.
 
I think i failed to mention im from ireland and we use a single pole switch fuse on our boards and in the uk you guys use a double pole. So without the main earth disconnected the N-E link would still exist for me.

Thanks for the replies lads!!!

The main Neozed switch fuse?
 

Reply to Insualtion resistance testing. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
463
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
362
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top