F

flyboy

can anyone help. when doing a ir test on ring cct i get a reaing n/l > 299 n/e >299 but l/e 148 this is on new wiring and same problem on three different ccts lighting cct 64 meg ohms nothing is plugged in anywhere all appliancies disconnected. though maybe a bit of bad cable but this is on 3 ccts seems a bit strange. have tested each indivdiual cable and they test ok but when put back together bad reading again. would appreciate any help. thanks dave
 
As Tel says, the readings are well within the guidelines set out by BS 7671?

Why would you think you have a 'bit of bad cable' on a newly installed circuit? Was it second hand Polish cable or something?
 
Just out of interest I did the old calculation of maximum leakage not being greater than 1/10,000[SUP]th[/SUP] of circuit FLC I was taught as an apprentice. That’s even more generous. For lighting on a 6A MCB it works out to 383K Ώ. For a RFC it’s 71K Ώ.
Remember I was playing about with VIR’s then.

The calculation is now used mainly for motors and PILC cables.
As I said I just did it out of interest.
 
With anything over 1meg deemed satisfactory, 2meg warranting further investigation....i would say that 148 is a bloody good reading, mark it off and move on to the next test - i wouldn't even bat an eyelid.
 
On single phase, I just link out the live bar feeding the breakers and protective device(s) at the bottom with the earth using abit of wire and croc-clips, then take the insulation reading between earth and neutral and if its over 2meg then it complys, if it isn't then test individually....and to be fair if it was a new install and it was anything as low as 2 i would rip it out and ------- the apprentice ha. Obviouslly do the test twice if theres 2 neutral's
 

Reply to insulation bad readings in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
403
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
991
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
356
Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
470
TerryBNZ
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top