Hello everyone. First post here.

I need to install some downlights into a kitchen ceiling, ideally LED. Above the ceiling is 10 inches of rockwool and then some underfloor heating pipes running at 50degC. Does anyone know of any lights that would be suitable?

Cheers,
Ken
 
LED fire rated fittings would be good but you will still need to clear the rockwool away from them and the driver/transformer.

You could cut out a square section of the ceiling at each point and cut out the rockwool then fit some battens re-fit the board then drill your holes for the downlights.
 
If I used Haler H2s say, and I made an enclosure to give the recommended 50mm air gap above, then that would give me only 50-100mm of rockwool between the enclosure and the ufh pipes. Should I be worried about the heat from above affecting the longevity of the electronics?
 
I has EXACTLY the same problem a couple of weeks ago. The Aurora ones are fine, but the cans on them are quite tall. Halers LED ones are only 80mm to the top, and having spoken to Halers tech desk, so long as you can get 50mm of space all around them (which is really only just pushing the insulation back around with your hand through the hole) then they are happy for them to co-exist with underfloor heating pipes.
 
I has EXACTLY the same problem a couple of weeks ago. The Aurora ones are fine, but the cans on them are quite tall. Halers LED ones are only 80mm to the top, and having spoken to Halers tech desk, so long as you can get 50mm of space all around them (which is really only just pushing the insulation back around with your hand through the hole) then they are happy for them to co-exist with underfloor heating pipes.

Ha!. small world. Thanks Rockingit.. that's good to hear.
 

Reply to Insulation coverable led downlights in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K
  • Question
Thanks for the input guys. Lighting track is out of the question. The routing (h section guirders and angle iron) means that swa cable clipped...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top