P

pencilpusher

I have been to a job today for a CU change. Quick test between N and E gave the following results:

2 RFC on RCD - downstairs 4.5M ohms, upstairs 2.2M ohms. No RCD tripping problems.

Non protected side - downstairs lighting 13M ohms, the remaining circuits 300M ohms.


Installation is 10 years old. No apparent alterations.

Any ideas where to start looking re RFC's and down lights please. I know they are within regs (just) but I would expect results to be higher than these three.

Thanks

PP
 
I tested the whole board initially but got low results so removed neutrals one at a time. On the non RCD side, when downstairs lights removed from neutral bar, I got 300M ohms for the rest in that bar and 13M ohms for the lighting (neutral removed and tested to whole earth bar) On RFC's I removed the neutrals and tested them seperately to whole earth bar. Should I test removed neutrals to removed CPC's?
 
Yes I would disconnect all 6 cables to each RFC and test, remember that Earths and Neutrals are commoned at the CU and you will never get the bottom of this if you have all sorts of variables in the mix.

Though I admire your dedication, as you point out these are acceptable, if low results, so how far are you going to go along with this?
 
Thanks Malcolm. I will do that. I am thorough and I will do the job but I like to just delve a bit to see if there is a serious underlying problem here. Although I am not doing a PIR here as such, I do wonder what this IR may be in 1 or 2 years time.

I am also hoping that with the new board, the RFC's won't start tripping out the RCD. The RFC's are not at the moment but with my luck they will start to!

I take your advice on dampness but is it possible it could be an issue at a socket for example?

Thanks

PP
 
Last edited by a moderator:
If you got these results on the L-N test then I would say that 95% you had a load still connected, but as it is on the N-E test then it's not a load, nor really can it be a dead short.

As you say the installation is 10 yrs old, so unless you have had some really heavy loads, or severely undersized cables unlikely that there is damage to the cables to allow the insulation to break down, so it is likely to be dampness somewhere, from either an outside accessory or damp from the walls.

Just go about it methodically, disconnect all the cables for the circuit to make sure they are completely separate from the others and test, then break the circuit down until you find it.
 

Reply to Insulation Reistance problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top