Hi all!

IR global test: line & neutral connected together and tested to earth @ 250v... (nothing disconnected) eventually climbs after 2 minutes to give a reading of 140Mohms. (dampness?)

When tested on 500v it just sits at 0.30Mohms ???

I have tried individual circuits in the same way but all seems the same values? Is it because nothing is disconnected as well as damp? (Its TNS 100ma rcd main board)

Thanks in advance :D
 
Ive never had it when it stays low at 500v but a rising reading as you say usually indicates dampness in the cable which when you whack voltage through it
 
Yeah, I mean it doesn't affect the present 100ma RCD. It was just a pre check before cu change but will this trip the 30ma rcd once changed over?? My tester has only been calibrated last week aswell so I'm confused.
 
Some electronic items do not like the global approach and whilst at 250v they can withstand the voltage upping it too 500v hurts them. As they are not designed to operate at 500v.
I suggest that you switch of isolators to fans, boilers, etc. even neons can give weird and wonderful results.
 
Ok -will do, thanks. There are 2 neons that might be doing this. I was under the impression that they wouldnt affect the l&n to earth test?

It looks like there is definitely dampness though. All circuits are in use and no outside lights some perhaps bathroom / kitchen circuits damp ingress.
 
The low resistance at 500v, is often caused by a surge protector multiblock that customers use for their IT or audio equipment. Find it and unplug before the 500v test.

The gradually increasing resistance reading is probably capacitance within an electronic module? Heating controllers or lights with pir's are the favourites. Both these things are unlikely to cause you a problem with a 30ma rcd but occasionally those cheap surge multiblocks will result in nuisance tripping.
 
Agree with all of the above. Some equipment just can't take 500v, even to earth. Remember, it's really the cabling you are checking and any equipment should be unplugged above 250v.
 

Reply to Insulation Resisitance (quick question!!) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
594
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
681
loz2754
L
  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
656

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top