Cornubian
Evening all. Thought I would finally seek advice of those who know better! This is my first post so be gentle with me!
Just wired a new 3 bed house. All great until I test for ins. res. on final lighting circuit. Result came in at less than 1Mohm- [ L-E = 0.39, LN-E = same ] did all the usual checks and soon got it down to the 3 and earth for the two way switches on stairs.
Now, if I isolate the cable in question, rest of the light circuit passes ins. test as expected.
If I link both switches with new cable [ just dangled on the floor ] test passes so switches are fine.
Fine, just to prove it is the cable in question I ins. test just the installed cable and it passes! I am now left wondering why this is? Am I missing something totally obvious here???
It also passed cont test as well.
Major frustration- as with all fault finding when on quote work although if I find it's a plasterboard screw then its happy days!
Thanks in advance for any help!
Just wired a new 3 bed house. All great until I test for ins. res. on final lighting circuit. Result came in at less than 1Mohm- [ L-E = 0.39, LN-E = same ] did all the usual checks and soon got it down to the 3 and earth for the two way switches on stairs.
Now, if I isolate the cable in question, rest of the light circuit passes ins. test as expected.
If I link both switches with new cable [ just dangled on the floor ] test passes so switches are fine.
Fine, just to prove it is the cable in question I ins. test just the installed cable and it passes! I am now left wondering why this is? Am I missing something totally obvious here???
It also passed cont test as well.
Major frustration- as with all fault finding when on quote work although if I find it's a plasterboard screw then its happy days!
Thanks in advance for any help!