I

iwire4

I have recently qualified and am coming towards testing a re-wire. I have fitted 30 low voltage downlighters with transformers. Apart from removing the bulbs do I need to do anything else before pumping 500volts through the circuits. ie will 500volts damage the transformers or are they removed from the circuit before this test, or done at 250volts? This has not been properly explained to me.
Any advice greatfully received.
Thanks.
 
You should've IR'd the circuit before fitting the transformers and you're going to have to remove or isolate them now to get a L/N reading.
You can test the individual units with L&N combined to E once they're removed if you like.
 
Agree with johnny-g much easier to do before fitting any lamps transformers, thermostats, etc you can see how to do the 250v test on youtube The learning lounge videos will help. I feel your tutors should have run through this along with live and dead testing and the order in which you do it, with you

Forgot to say dont forget the Electric shower and Hob very sensitive components . The tests are known as tests 1 and 2 if it helps you looking.
 
Guys, thanks for the advice. Makes sense and I could have saved myself some work if I had asked the question before. A lesson learnt not to be forgotten. I need some lessons in using this forum as well. Apologies for the late reply.
Cheers.
 

Reply to Insulation resistance low voltage lighting in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
485
For my hapeneth and learnt from hard recent experience, the term LED transformer and driver tend to be used interchangeably, when they are...
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top