Hi all
I am practising with my megger 1553 and when doing a IR test in my ring socket circuit and I put the probes onto Neutral - Earth I get a reading of 7,31 m Ohms.
Is this acceptable?
And also am I doing the test correctly (for the explained problem above):
Its an existing instalation:
- Main Switch OFF
- Circuit Breaker for the Ring Circuit ON
- All socket outlets switched ON
- Probes to N-E
- Press Test button
- Take reading 7,31 M Ohms
NOTE: When testing the N-L & L-E readings are both >299
Am I doing it right or have I got switches in wrong positions etc AND/OR is it best to test the above way (from OSG) or is it better to disconnect L,N & E cables of the individual circuit to be tested and place croc clips on the specific circuit cables and test?