elecypwn
Hey guys! first real post on the forum so be gentle!
Basically i have installed a new installation feeding a new cinema room, it has 8 mains powered down lighters ( no transformer ) and 2 wall lights, When i tested the installation for IR i got the following results:
L-N - 1000 M ohms
L-E - varies from 300 -500 M ohms
N-E - Varies from 300-500 M ohms
This is a brand new installation, that has been installed behind plasterboard so at least to my knowledge there can be no moisture, there is no screws/nail penetration and all my terminals are sound and tight with in Junction boxes and light fittings, there not hooked up to the consumer unit yet, testing has been done from the cable that will be entering the board.
Another strange thing is, i disconnected the wall lights from the circuit and tested that individually, that was sound, then i tested the 8 down lighters again and still had the persisting problem! now the weird bit! i disconnected the cable entering the choc box that been fed from the switch live to feed the first light so the daisy chain cables feeding the lights were separate, and the cables from the consumer unit to the switch were separate, now when i tested both them separatly the readings where spot on all 1000+ but when i connected them back into the choc box i got the same weird results, so took them back out, split them tested the cable feeding the lights, sound, tested the incoming cable to first light, through the switch back to the consumer unit, them results were sound, connected them back up again, Weird reading! can somebody tell me what the hell could be going on please xD
also iv never had this problem before and relied on my >1000MOhm readings, if i interpret the regs correctly would a 300-500Mohm reading be a pass anyway? would 1.0M ohm be just 1.0M ohm on my tester ( metrel easi multi tester )? but id ideally like it all to be >1000, could my 300-500Mohm readings be acceptable on a test cert? cheers
Basically i have installed a new installation feeding a new cinema room, it has 8 mains powered down lighters ( no transformer ) and 2 wall lights, When i tested the installation for IR i got the following results:
L-N - 1000 M ohms
L-E - varies from 300 -500 M ohms
N-E - Varies from 300-500 M ohms
This is a brand new installation, that has been installed behind plasterboard so at least to my knowledge there can be no moisture, there is no screws/nail penetration and all my terminals are sound and tight with in Junction boxes and light fittings, there not hooked up to the consumer unit yet, testing has been done from the cable that will be entering the board.
Another strange thing is, i disconnected the wall lights from the circuit and tested that individually, that was sound, then i tested the 8 down lighters again and still had the persisting problem! now the weird bit! i disconnected the cable entering the choc box that been fed from the switch live to feed the first light so the daisy chain cables feeding the lights were separate, and the cables from the consumer unit to the switch were separate, now when i tested both them separatly the readings where spot on all 1000+ but when i connected them back into the choc box i got the same weird results, so took them back out, split them tested the cable feeding the lights, sound, tested the incoming cable to first light, through the switch back to the consumer unit, them results were sound, connected them back up again, Weird reading! can somebody tell me what the hell could be going on please xD
also iv never had this problem before and relied on my >1000MOhm readings, if i interpret the regs correctly would a 300-500Mohm reading be a pass anyway? would 1.0M ohm be just 1.0M ohm on my tester ( metrel easi multi tester )? but id ideally like it all to be >1000, could my 300-500Mohm readings be acceptable on a test cert? cheers