Howdy folks.
I am working my way through loads of past test papers at the moment in preparation for my July exam.
I have been asked to insulation test a ring that has been properly isolated.
The way I have always insulation tested rings is to remove line, neutral and CPC conductors from the board, join L1L2, join N1N2 and join CPC1CPC2 then test at 500v between each (with all equipment removed)
I like this method.
I notice in GN3 that they like you to leave the conductors in the board and test between L and N and E (line at the outgoing side of the isolated MCB, Neutral simply connect a crocodile clip to the neutral bar and CPC simply connect a crocodile clip to the CPC/ Earth bar.
Do you think my method of removing all conductors from the board will lose me marks and do you think it is a waste of time removing these conductors?
Tanks a million.
 
Last edited:
as long as you isolate befoer testing, there is no need to remove conductors from CU .i would only do this if i got a bad reading that had to be investigated.
 

Reply to Insulation resistance of ring, 2391 question again!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
283
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top