how would you calculate the insulation resistance on domestic ring circuit when measuring with both live and neutral conductors connected together to the circuit protective conductor, is there any way of calculating the approximate value before using a insulation resistance instrument. cheers
 
I'm not sure I understand the question!

my question was that instead of testing live to earth and neutral to earth separately, connect both conductors to one lead of the tester and other lead to earth, the reason I am asking this question is because recently I was carrying out a test on a ring circuit run in twin and earth, when testing live to earth and neutral to earth separately I obtained values of resistance greater than >9000 when both live and neutral are connected together on one lead of the instrument and the second lead to earth my insulation resistance was less than half on a short test and would increase on a 30 second test, is this just due to the increase in parallel paths.
 
When you're carrying out an IR test you're not supposed to have any parallel paths connected mate. You haven't really thought this question out have you?
 
I think what our man means here, is that L & N are in parallel, so you could expect half the single L/N-E test results.
Also, twice the cable length under test, so it'd take longer to charge up.


Disclaimer, it's late and I've had loadsa beer! :-)
 
You can as a minimum IR between live conductors to CPC. Preferable to do all three though. Zap L - N at 250V to see if anything may still be connected. But, No, you can't calculate IR test results, have to measure them..

Are you getting mixed up with r1r2/4 continuity tests etc perhaps?!

Just read your second post, if you are getting >9000 meg ohms for L-CPC and N-CPC then measure L-N and be happy! Don't worry yourself measuring LN-CPC. What tester you using?
Remember in T&E the CPC isn't insulated, which would have a bearing possibly.
 
There is a calculation for minimum insulation resistance which the IET have conveniently swept under the carpet in favour of a one size fits all figure of 1MΩ
 
I am quite certain that there must be calculations that are employed by the cable manufactures to determine the effects of parallel paths and insulation resistance over a given length.
cheers
 
I am quite certain that there must be calculations that are employed by the cable manufactures to determine the effects of parallel paths and insulation resistance over a given length.
cheers

There is a calculation for 'parallel paths' as you call them. We all learned it at school, and then went over it again when training to be electricians. Does 1/R = 1/R1 + 1/R2 + 1/R3 ....... + 1/Rn ring any bells with you?
 
my question was that instead of testing live to earth and neutral to earth separately, connect both conductors to one lead of the tester and other lead to earth, the reason I am asking this question is because recently I was carrying out a test on a ring circuit run in twin and earth, when testing live to earth and neutral to earth separately I obtained values of resistance greater than >9000 when both live and neutral are connected together on one lead of the instrument and the second lead to earth my insulation resistance was less than half on a short test and would increase on a 30 second test, is this just due to the increase in parallel paths.
Just out of interest,when you say "half",do you mean half of >9000 or half a M Ohm? Also,there is a difference between parallel paths and resistances in parallel. The difference between your two IR readings,if known for sure,would help explaining what may be occurring.Thanks
 
Why not just measure IR like normal?

Trev is right why complicate things...... lifes hard enough!!!! :banghead:

Quite simple, the IET’s one size fits all doesn’t fit in the real world.

When you’re faced with 500yards of 0.3²” 3c PILC SWA that’s over 50 years old, are you going to replace it? 0.3 is about 240mm.
A large motor (100’s of HP not some piddling little thing) are you going to replace it?

You work out the minimum acceptable resistance and then use your experience to say if it’s a goer or not.
Before I condemned anything I made damned sure I was right.

Regarding the 50 year old cables, they were that old before I diverted them for reuse 25 years ago. 75 years old and still in service to this day.

Believe it or not dazza, we had electric long before the 17[SUP]th[/SUP] edition.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
insulation resistance on a domestic ring circuit
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
mk1,
Last reply from
Knobhead,
Replies
18
Views
4,985

Advert

Back
Top