During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth.
When I disconnected the neutral from the neutral bar it's 116 MegOhms lowest (on the outside bollards).

However measuring from disconnected neutrals to earth all read over 200 MegOhms.

So it does not comply as measured but complies with neutral disconected.

Does anyone have an idea why? [ElectriciansForums.net] Insulation resistance problems
 
TL;DR
Interesting IR readings
What voltage were you using for the IR test? Maybe the neutral was being pulled down to earth via surge arrestors somewhere on another circuit.
 
If I understand you right, every circuit individually achieves over 200MΩ but when the neutrals are commoned, one circuit reads 1.4kΩ L-E? Do we know what the aggregate N-E reading was at that moment? You mention bollards; presumably this means permanently-connected lighting loads (on which we preferably wouldn't be testing L-E and N-E separately.) If there was any kind of N-E fault anywhere on any circuit, commoning the neutrals with it will equally affect the line on any circuit with load. I would be wondering what if anything was disturbed that created an intermittent low IR on the neutral bar, even if it only happened to manifest while testing the line.
 

Reply to Insulation resistance problems in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
285
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top