I am going to do my first install and at the risk of getting shot down, I was told on my training that you can NOT do a insulation resistance test dc side? However since been told by a friend that is wrong! Can someone please tell me the exact sequence, as everyone has a different take on this. I don't wish to name the training provider but I hear the nic do it somewhat different and ask for more results than the others. Hope that is as clear as mud, just want to know how it's done!
 
Page 53 of the DTI Guide to installing PV Systems:

Two Methods:
a) Test between array negative and earth followed by test between Array positive and earth
or
b) Test between earth and short-circuited Array Negative and Positive.
 
Was told on my training course (2399) to test both +ve and -ve to earth an to set the tester to 500v to testand not 1000 as max cable rating is 1000v and your test equiptment could well deliver +/- 5%
 

Reply to Insulation resistance test dc side in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
741

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top