This is to do with Periodic Inspections. When you are testing a circuit and forget to unplug a piece of equipment that has a high earth leakage could this be damaged doing the ins res test between live and earth. I do not know electronics but is there a connection to earth. The problem has always been, up to now, live/neutral test but i now have doubts about live/earth. Interested to see your views.
Thanks Daisy.
 
You could certainly damage the filters/surge suppressors on the input of the equipment.

Try to remove all equipment.

Test at a lower voltage first. If you get leakage, don't go to higher voltage without investigating first.
 
Maybe, I wouldn't like to try it. Always test at 250v before you do 500v then if you get a low reading you can investigate why (eg equipment plugged in) before you risk doing damage.
 
Thanks guys.
That has been my trick over the years,start with 230v and see if it is a low reading live/neutral to earth. But someone has said to me this could damage equipment because the test voltage is DC.
Any thoughts.
Thanks Daisy
 

Reply to insulation resistance test on equipment with high earth leakage in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
153
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
515
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
459

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
307
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top