I'm using a Fluke 1652c as my MFT. When I do the Insulation resistance tests at 500v - sometimes the result is displayed immediatley i.e >500 Megohms , other times the resistance seems to climb slowly, peaking around a figure. As this figure is generally massively in excess of the required 2 Megohms should I be worried about it ? Why would the level of resistance climb if the voltage remained consistent?
 
also, sometimes a slight bit of damp can give you a low reading, rising as the 500v dries it out.
 

Reply to Insulation Resistance Test with Fluke 1652 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top