Hi guys, I'm currently studying level 3 c&g 2330, and have my testing exam coming up very shortly. I was wondering if there was more than 1 way to test insulation resistance, and if so which is the most common because 1 of the lecturers told me: with the main isolator locked off, with the tester set to 500v,all 500v harmed disconnected, and all mcb's and switches on, at the bottom of the main isolator switch in the c.u probe between Line & neutral, then Line at same point to main earth bar, and finally Neutral at bottom of main isolator to main earth bar. Then when I was practicing testing at college the other day a different lecturer said I should: with all mcb's & switches on, probe between any mcb and main earth bar, any mcb and main neutral bar(terminal) and between earth and neutral bars. Now I am confused, can anybody shed some light please? One last point, if testing ins. res with tester set to 200 mega ohms and a reading that says (overange 1) what do I write in the test box, simply 200 mega ohms or is it >200 mega ohms.
 
Both right (in a way) 1st teacher is more closer to GN3 (starts page 37) 2nd teacher is testing each circuit individually.(Generally done if IR is low (parallel resistances) (Bit more time consuming) If you have full control of the installation then 1st teacher method is best and quickest. Tests whole installation greater than 1mohm, job done. If its more than 200m ohm then put >200m ohm in the box.

Don't forget to flick the switching on any two way and or intermediate lighting (page 39 GN3)

Read GN3 from page 37, its self explanitary

Markysparky
 
Hi guys, I'm currently studying level 3 c&g 2330, and have my testing exam coming up very shortly. I was wondering if there was more than 1 way to test insulation resistance, and if so which is the most common because 1 of the lecturers told me: with the main isolator locked off, with the tester set to 500v,all 500v harmed disconnected, and all mcb's and switches on, at the bottom of the main isolator switch in the c.u probe between Line & neutral, then Line at same point to main earth bar, and finally Neutral at bottom of main isolator to main earth bar. Then when I was practicing testing at college the other day a different lecturer said I should: with all mcb's & switches on, probe between any mcb and main earth bar, any mcb and main neutral bar(terminal) and between earth and neutral bars. Now I am confused, can anybody shed some light please? One last point, if testing ins. res with tester set to 200 mega ohms and a reading that says (overange 1) what do I write in the test box, simply 200 mega ohms or is it >200 mega ohms.

The first method is what we refer to as a global IR test, this is a great time saver but only really practical on simple installations.

If the reading (s) on the global IR test are unsatisfactory then the installation should be IR tested circuit by circuit (as per lecturer 2) to identify where the low IR reading is coming from.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Insulation Resistance test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
sparko,
Last reply from
IQ Electrical,
Replies
2
Views
7,613

Advert

Back
Top